Ziegler-Nichols PID Tuning Guide
A short quick guide to PID tuning using the Ziegler-Nichols method.
Ziegler-Nichols Method
One of the most straightforward methods to tune PID controllers is the Ziegler-Nichols method, which provides a systematic way to find initial PID gains based on the systemโs response.
Here is an example of the velocity PID tuning process using this method. But the similar process can be applied to current PID tuning as well as for the position PID (with some adjustments to the target and monitoring variables).
Step 1: Find Critical Gain
Start with I and D disabled:
motor.PID_velocity.P = 0.1; // Start low
motor.PID_velocity.I = 0.0;
motor.PID_velocity.D = 0.0;
Use the motor.monitor() to observe the velocity response while gradually increasing P:
// Example monitoring setup (velocity + target)
// ... motor, sensor, driver init ...
motor.monitor_variables = _MON_TARGET | _MON_VEL;
motor.monitor_downsample = 10; // print every 10th loop
// ... motor.init(); motor.initFOC(); ...
// main FOC algorithm
// hold a constant velocity target for tuning
motor.move(5.0); // rad/s
// print monitoring data
motor.monitor();
Increase P gradually until the system oscillates continuously.
Note two values:
- Kc = the P value where oscillation starts
- Tc = period of oscillation (seconds) - the time between peaks in the velocity response
Example: Oscillation at P = 0.8 with period 0.1s โ Kc = 0.8, Tc = 0.1
Step 2: Apply Formula
Choose your controller type:
P Only
P = 0.5 * Kc;
PI (Most Common)
P = 0.45 * Kc;
I = 0.54 * Kc / Tc;
D = 0.0;
PID
P = 0.6 * Kc;
I = 1.2 * Kc / Tc;
D = 0.075 * Kc * Tc;
Example: Calculate PI Gains
Given Kc = 0.8, Tc = 0.1:
motor.PID_velocity.P = 0.45 * 0.8 = 0.36;
motor.PID_velocity.I = 0.54 * 0.8 / 0.1 = 4.32;
Fine-Tuning After Ziegler-Nichols
Minor adjustments after applying the formula:
Oscillating? โ Reduce I by 20-50%
Too slow? โ Increase P or I by 20%
Overshooting? โ Reduce P by 10-20% or add D = 0.001รP
Parameter Effects
| Parameter | Too High | Too Low |
| P | Oscillation | Slow, steady-state error |
| I | Overshoot, oscillation | Drifts from target |
| D | Noise amplification | Overshoot |
| output_ramp | Sluggish | Jerky motion |
| limit | No protection | Saturation |
Common Fixes
| Problem | To tryโฆ |
| Oscillating | Reduce P or I by 50% |
| Slow | Increase P or I |
| Overshoot | Reduce P/I or add small D |
| Steady error | Increase I |
| Jittery | Increase LPF_velocity.Tf or set D = 0 |
Related Documentation
PID controller implementation Tuning velocity loop Low-pass filter implementation